Revpi core 3 modbus TCP salve and Revpi DIO
-
- Posts: 30
- Joined: 03 Sep 2018, 10:01
Revpi core 3 modbus TCP salve and Revpi DIO
We use Revpi core 3 connected two Revpi DIO,in Pictory,we give the Revpi core 3 for virtual Modbus tcp slave,the slave have 32 inputs and 32 output,and the two Revpi DIO also have 32 inputs and 32 outputs totally.How do we match the virtual Modbus tcp Master and physical DIO modules?
- RevPiModIO
- KUNBUS
- Posts: 322
- Joined: 20 Jan 2017, 08:44
- Contact:
Re: Revpi core 3 modbus TCP salve and Revpi DIO
You can use a simple Python program to mirror the IOs of your devices.
The easiest solution is this little Python program, which mirrors your IOs using a dictionary with piCtory names. If the input value of "I_1" of die DIO is True, than the program will write a "1" to "Output_15" which you can read with Modbus. If you write a value >0 to an Input of the ModbusSlave, than the associated Output of the DIO will be set to True.
This is a kind of 1:1 mirroring if you use the 34/32 mode for the DIOs in piCtory. If you use 19/17 mode, all 16 Bits of Input / Output will be available as one Word, which you can mirror to just one input / output of Modbus, but you have to split this bits with your ModbusMaster.
To transfair, start and watch the program, you can install RevPiPyLoad. The daemon will execute it on Revolution Pi startup and let it run all the time: https://revpimodio.org/en/revpipyplc-2/
Sven
The easiest solution is this little Python program, which mirrors your IOs using a dictionary with piCtory names. If the input value of "I_1" of die DIO is True, than the program will write a "1" to "Output_15" which you can read with Modbus. If you write a value >0 to an Input of the ModbusSlave, than the associated Output of the DIO will be set to True.
This is a kind of 1:1 mirroring if you use the 34/32 mode for the DIOs in piCtory. If you use 19/17 mode, all 16 Bits of Input / Output will be available as one Word, which you can mirror to just one input / output of Modbus, but you have to split this bits with your ModbusMaster.
Code: Select all
#!/usr/bin/python3
# -*- coding: utf-8 -*-
"""Modbus IO-mirror."""
__author__ = "Sven Sager"
__copyright__ = "Copyright (C) 2018 Sven Sager"
__license__ = "GPLv3"
import revpimodio2
def cleanup():
u"""Clean IOs of RevPi."""
rpi.core.a1green.value = False
def cycle(ct):
u"""Cycle to mirror the IOs."""
# Flash A1 led just to see the program is running
rpi.core.a1green.value = ct.flag10c
# Mirror data
for input_name in dict_io_map:
rpi.io[dict_io_map[input_name]].value = int(rpi.io[input_name].value)
# Create RevPiModIO and pass cleanup function
rpi = revpimodio2.RevPiModIO(autorefresh=True)
rpi.handlesignalend(cleanup)
# Create IO mapping input: output
# The names are the names which you define on piCtory!
dict_io_map = {
# DIO 1 inputs to first 14 Outputs of ModbusMaster
"I_1_i09": "Output_1",
"I_2_i09": "Output_2",
"I_3_i09": "Output_3",
"I_4_i09": "Output_4",
"I_5_i09": "Output_5",
"I_6_i09": "Output_6",
"I_7_i09": "Output_7",
"I_8_i09": "Output_8",
"I_9_i09": "Output_9",
"I_10_i09": "Output_10",
"I_11_i09": "Output_11",
"I_12_i09": "Output_12",
"I_13_i09": "Output_13",
"I_14_i09": "Output_14",
# DIO 2 inputs to next 14 Outputs of ModbusMaster
"I_1": "Output_15",
"I_2": "Output_16",
"I_3": "Output_17",
"I_4": "Output_18",
"I_5": "Output_19",
"I_6": "Output_20",
"I_7": "Output_21",
"I_8": "Output_22",
"I_9": "Output_23",
"I_10": "Output_24",
"I_11": "Output_25",
"I_12": "Output_26",
"I_13": "Output_27",
"I_14": "Output_28",
# First 14 inputs of ModbusMaster to DIO 1
"Input_1": "O_1_i09",
"Input_2": "O_2_i09",
"Input_3": "O_3_i09",
"Input_4": "O_4_i09",
"Input_5": "O_5_i09",
"Input_6": "O_6_i09",
"Input_7": "O_7_i09",
"Input_8": "O_8_i09",
"Input_9": "O_9_i09",
"Input_10": "O_10_i09",
"Input_11": "O_11_i09",
"Input_12": "O_12_i09",
"Input_13": "O_13_i09",
"Input_14": "O_14_i09",
# Next 14 inputs of ModbusMaster to DIO 2
"Input_15": "O_1",
"Input_16": "O_2",
"Input_17": "O_3",
"Input_18": "O_4",
"Input_19": "O_5",
"Input_20": "O_6",
"Input_21": "O_7",
"Input_22": "O_8",
"Input_23": "O_9",
"Input_24": "O_10",
"Input_25": "O_11",
"Input_26": "O_12",
"Input_27": "O_13",
"Input_28": "O_14",
}
# Start mirroring
rpi.cycleloop(cycle)
To transfair, start and watch the program, you can install RevPiPyLoad. The daemon will execute it on Revolution Pi startup and let it run all the time: https://revpimodio.org/en/revpipyplc-2/
Sven
python3-RevPiModIO - https://revpimodio.org/ || Der RevPi ist das Beste, was passieren konnte!
Re: Revpi core 3 modbus TCP salve and Revpi DIO
nice example ! it should be saved in download section
- krambambuli
- Posts: 68
- Joined: 18 Jun 2018, 09:56
Re: Revpi core 3 modbus TCP salve and Revpi DIO
Nice example! Thank you.
Is there also a code snipped for the other direction? To set outputs externally via modbus.
Is there also a code snipped for the other direction? To set outputs externally via modbus.